Re: [Apcupsd-users] apcupsd not showing any UPS load
Brought to you by:
adk0212
|
From: Trev <tr...@se...> - 2025-11-27 05:15:14
|
Jeffery Small wrote on 27/11/25 10:56 am: > Xubuntu: 24.04.3 > apcupsd: 3.14.143.1build2 (standard Ubuntu package) > UPS: New APC SMC1500C with USB connection > > I just built a new Linux workstation with a new APC UPS. Everything is > running fine except that the monitor is showing no load despite all of > my equipment plugged into the UPS. Here is a link to a screenshot: > > http://cjsa.com/misc/apcupsd_01.png > > Any reason that this is happening? On my previous system with the same UPS > which was more than five years old, all of this worked fine. Could this > be a configuration issue? It is unclear to me whether you are using the same UPS. You say it's a new APC UPS and later the same UPS. I'd hazard a guess that it is a new UPS and very probably has a different firmware. APC's USB firmware versions have been notoriously buggy. Is there a firmware update for the new UPS? If so, apply it and hope. Alternatively: 1) try the modbus protocol as someone has already helpfully suggested; or 2) try a USB->RS232 converter if you have a serial port on your new computer. |