Re: [Apcupsd-users] APC Smart-UPS 3000 RM bad batteries or just failing?
Brought to you by:
adk0212
|
From: Kris J. <apc...@sa...> - 2013-02-26 20:03:11
|
How old is the UPS? Can you check the float voltage with a good voltmeter? Smart-UPS's seem to have a tendency to overcharge the batteries causing early failure. Some models can be adjusted by software. Jonathan Murray wrote, On 2/26/2013 10:33 AM: > I've got 3: > > APCMODEL : Smart-UPS 3000 RM > > On some of these units, which happen to be all in the same rack, the > battery status switches to: > > STATUS : ONLINE REPLACEBATT > > This happens at all levels of load. If I shut down the systems connected > to it, shut off the UPS, I can get about 3 weeks with the STATUS: > ONLINE, then it switches to ONLINE REPLACEBATT. > > The batteries were replaced July 7, 2012. (batteryspec.com), This was > the first battery replacement for these units. > > Has anyone else seen this behavior or have any clues? I'm thinking > either the batteries are poor quality, or the charging systems in the > UPSes have failed or aren't operating normally. > > Thank you > > |