Re: [Apcupsd-users] Configuring external battery packs
Brought to you by:
adk0212
|
From: Brother R. of R. <al...@ca...> - 2011-07-16 04:09:26
|
On Sat, Jul 16, 2011 at 11:58:07AM +1000, Trevor Roydhouse wrote: > Brother Railgun of Reason wrote: > > > Hi, > > I have an APC SU3000RMXL3U, to which I just added an SU48R3XLBP battery > > pack. Everything connected just fine physically, but the UPS still > > reports 0 external battery packs connected. > [...] > > Is there any way I can perform this setting using apcupsd (3.14.8), or > > is this a case where I really have to have either PowerChute Business or > > network management? > > The setting is available via a terminal program or apctest's termnal > mode, at least if you have a serially connected UPS. > > See http://apcupsd.org/manual/manual.html#the-smart-protocol for details > of changing it. Thank you kindly. :) That should be all I need. -- Phil Stracchino, CDK#2 DoD#299792458 ICBM: 43.5607, -71.355 al...@ca... al...@me... ph...@co... Renaissance Man, Unix ronin, Perl hacker, SQL wrangler, Free Stater It's not the years, it's the mileage. |