Re: [Apcupsd-users] Configuring external battery packs
Brought to you by:
adk0212
|
From: Trevor R. <tr...@se...> - 2011-07-16 01:58:19
|
Brother Railgun of Reason wrote: > Hi, > I have an APC SU3000RMXL3U, to which I just added an SU48R3XLBP battery > pack. Everything connected just fine physically, but the UPS still > reports 0 external battery packs connected. [...] > Is there any way I can perform this setting using apcupsd (3.14.8), or > is this a case where I really have to have either PowerChute Business or > network management? The setting is available via a terminal program or apctest's termnal mode, at least if you have a serially connected UPS. See http://apcupsd.org/manual/manual.html#the-smart-protocol for details of changing it. -- Trevor Roydhouse BJuris, LLB, LLM (UNSW) Systems Developer Australasian Legal Information Institute Web : www.austlii.edu.au |