    I have one question though:

    What firmwares are supported with Moka7??
    I have a S7-1200 FW3.0 and cant get the setup to work propperly. The testprogram outputs the folowwing:

    +================================================================
    | ConnectTo()
    +================================================================
    Connected to : 10.0.0.150 (Rack=0, Slot=0)
    PDU negotiated : 240 bytes
    Execution time 16 ms

    +================================================================
    | GetOrderCode()
    +================================================================
    Order Code : 6ES7 214-1AG31-0XB0
    Firmware version : 3.0.2
    Execution time 16 ms

    +================================================================
    | GetCpuInfo()
    +================================================================
    S7 function refused by the CPU.
    Execution time 4 ms

    +================================================================
    | GetCpInfo()
    +================================================================
    Max PDU Length : 240
    Max connections : 55
    Max MPI rate (bps): 0
    Max Bus rate (bps): 0
    Execution time 5 ms

    +================================================================
    | GetProtection()
    +================================================================
    S7 function refused by the CPU.
    Execution time 4 ms

    +================================================================
    | GetPlcDateTime()
    +================================================================
    S7 function refused by the CPU.
    Execution time 4 ms

    +================================================================
    | SetPlcSystemDateTime()
    +================================================================
    S7 function refused by the CPU.
    Execution time 26 ms

    +================================================================
    | ReadSZL() - ID : 0x0011, IDX : 0x0000
    +================================================================
    LENTHDR : 28
    N_DR : 3
    Size : 84
    00 01 36 45 53 37 20 32 31 34 2d 31 41 47 33 31 ..6ES7 214-1AG31
    2d 30 58 42 30 20 20 20 00 01 20 20 00 06 36 45 -0XB0 .. ..6E
    53 37 20 32 31 34 2d 31 41 47 33 31 2d 30 58 42 S7 214-1AG31-0XB
    30 20 20 20 00 01 20 20 00 07 36 45 53 37 20 32 0 .. ..6ES7 2
    31 34 2d 31 41 47 33 31 2d 30 58 42 30 20 20 20 14-1AG31-0XB0
    56 03 00 02 V...
    Execution time 4 ms

    +================================================================
    | GetPlcStatus()
    +================================================================
    PLC Status : RUN
    Execution time 4 ms

    +================================================================
    | PlcStop()
    +================================================================
    S7 function refused by the CPU.
    Execution time 5 ms

    +================================================================
    | PlcHotStart()
    +================================================================
    S7 function refused by the CPU.
    Execution time 4 ms

    +================================================================
    | GetAgBlockInfo()
    +================================================================
    S7 function refused by the CPU.
    Execution time 3 ms

    +================================================================
    | DBGet()
    +================================================================
    S7 function refused by the CPU.
    Execution time 4 ms

    +================================================================
    Tests performed : 13
    Passed : 5
    Failed : 8
    +================================================================

    Any Ideas?

     