To make MN to enter NMT_MS_BASIC_ETHERNET state, kindly set "NMT_StartUp_U32.Bit13 (1f80)" to 1 in openCONFIGURATOR.
In this state, MN may perform Legacy Ethernet communication according to IEEE 802.3 and there is no POWERLINK specific network traffic control.
Thanks,
Powerlink-Team-Kalycito
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Why my MN do not transition into "Basic Ethernet Mode"? showed as the picture below
picture
Hello Liu zhi qiang,
To make MN to enter NMT_MS_BASIC_ETHERNET state, kindly set "NMT_StartUp_U32.Bit13 (1f80)" to 1 in openCONFIGURATOR.
In this state, MN may perform Legacy Ethernet communication according to IEEE 802.3 and there is no POWERLINK specific network traffic control.
Thanks,
Powerlink-Team-Kalycito