    I took the openPOWERLINK_CN.xdd file that came with and added one  8bit input and one 8bit output like this:
    
    <object Index="6000" name="DigitalInput_00h_AU8" objectType="8" dataType="0005">
    <SubObject SubIndex="00" name="NumberOfEntries" objectType="7" #dataType="0005"          accessType="const" defaultValue="0x1" PDOmapping="no"/>
    <SubObject SubIndex="01" name="DigitalInput" objectType="7" dataType="0005" accessType="rw" PDOmapping="TPDO"/>
    </ Object>
    
    <object Index="6200" name="DigitalOutput_00h_AU8" objectType="8" dataType="0005">
    <SubObject SubIndex="00" name="NumberOfEntries" objectType="7" dataType="0005" accessType="const" defaultValue="0x1" PDOmapping="no"/>
    <SubObject SubIndex="01" name="DigitalOutput" objectType="7" dataType="0005" accessType="rw" PDOmapping="RPDO"/>
    </ Object>
    
    I then mapped my variables like this:
    
    <object Index="1A00" name="PDO_TxMappParam_0h_AU64" objectType="8">
    <SubObject SubIndex="00" name="NumberOfEntries" objectType="7" dataType="0005" accessType="rw" PDOmapping="no" defaultValue="1" />
    <SubObject SubIndex="01" name="ObjectMapping" objectType="7" dataType="001B" accessType="rw" PDOmapping="no" defaultValue="0x0008000000016000"/> 
    </ object>
    
    <object Index="1600" name="PDO_RxMappParam_0h_AU64" objectType="8">
    <SubObject SubIndex="00" name="NumberOfEntries" objectType="7" dataType="0005" accessType="rw" defaultValue="0" PDOmapping="no" />
    <SubObject SubIndex="01" name="ObjectMapping" objectType="7" dataType="001B" accessType="rw" PDOmapping="no" defaultValue="0x0008000000016200"/> 
    </ object>
    
    Then I started the openConfigurator, startet a new project and added a CN node. I replaced xdd file by right-click CN node and choose my openPOWERLINK_CN.xdd modified file. After this auto generation conditioned I MN node and built the project. Everything seems to work and I get a xap.h file that looks like this:
    
    / * This file was auto-generated by openCONFIGURATOR-1.2.2 on 07-May-2013 18:18:30 * /
    # ifndef XAP_h
    # define XAP_h
    
    # Define COMPUTED_PI_OUT_SIZE 4
    typedef struct
    {
        unsigned CN1_M00_DigitalInput_00h_AU8_DigitalInput: 8;
        unsigned PADDING_VAR_1: 24;
    PI_OUT};
    
    # Define COMPUTED_PI_IN_SIZE 4
    typedef struct
    {
        unsigned CN1_M00_DigitalOutput_00h_AU8_DigitalOutput: 8;
        unsigned PADDING_VAR_1: 24;
    PI_IN};
    
    # endif
    
    The problem is that in my mnobd.txt file looks like this:
    
    00000013
    / / / / Assignment nodeid
    1F81 01 00000004 00000007
    
    1A00 00 00000001 00
    1600 00 00000001 00
    1006 00 00000004 0000c350
    1C02 01 00000004 00000028
    1C02 03 00000004 00000028
    1C09 01 00000004 00000028
    1C14 00 00000004 02faf080
    1F26 01 00000004 000029df
    1F27 01 00000004 03edb4f0
    1F92 01 00000004 00006978
    1800 01 00000001 01
    1A00 01 00000008 000800000001A040
    1400 01 00000001 01
    1600 01 00000008 000800000001A4C0
    1A00 00 00000001 01
    1600 00 00000001 01
    / / / / Configuration data for CN-1
    1F22 01 00000066
    0000000a
    1600 00 00000001 00
    1A00 00 00000001 00
    1006 00 00000004 0000c350
    1020 01 00000004 000029df
    1020 02 00000004 03edb4f0
    1C0B 03 00000004 00000050
    1C0D 03 00000004 00000050
    1C14 00 00000004 02faf080
    1600 00 00000001 01
    1A00 00 00000001 01
    / / / / Nodeid Reas Sign Ment
    1F81 01 00000004 80000007
    
    It's doing something with my PDO_TX / PDO_RX (1A00/1600) but the folders are not my registry 6000/01 and 6200/01. It should look like this at the end of my mnobd.txt file:
    
    / / / / Configuration data for CN-1
    1F22 01 00000192
    0000001E
    1600 00 00000001 00
    1A00 00 00000001 00
    1006 00 00000004 0000C350
    1020 01 00000004 000029df
    1020 02 00000004 02f5a120
    1C0B 03 00000004 00000050
    1C0D 03 00000004 00000050
    1C14 00 00000004 02faf080
    1600 01 00000008 0008000000016200
    1A00 01 00000008 0008000000016000
    1600 00 00000001 01
    1A00 00 00000001 01 
    / / / / Nodeid Reassignment
    1F81 01 00000004 80000007
    
    Does anyone have an idea why this doesn't work? I will also include my XDD and project file below.
    
     

    Last edit: Sixten Isaksson 2013-05-07
  • Sixten Isaksson

    Sixten Isaksson - 2013-05-07

    Xdd file..

     

    Last edit: Sixten Isaksson 2013-05-07
  • Sixten Isaksson

    Sixten Isaksson - 2013-05-07

    openConfigurator project..

     
  • Powerlink-team Kalycito

    Hello Sixten,

    From your first post we see that in
    object Index="1A00", SubIndex="01" the defaultValue field has been edited as "0x0008000000016000" but defaultValue field is not written to CDC file.

    Instead the defaultValue field should be left as "0x0" and the actualValue field is to be added as shown below,
    object Index="1A00", SubIndex="01" actualValue="0x0008000000016000" defaultValue="0x0"

    Then the output would resemble the below,

    / / / / Configuration data for CN-1
    1F22 01 00000084
    0000000C
    1600 00 00000001 00
    1A00 00 00000001 00
    1006 00 00000004 0000c350
    1020 01 00000004 000029df
    1020 02 00000004 02651150
    1C0B 03 00000004 00000050
    1C0D 03 00000004 00000050
    1C14 00 00000004 02faf080
    1600 01 00000008 0008000000016200
    1A00 01 00000008 0008000000016000
    1600 00 00000001 01
    1A00 00 00000001 01
    //// NodeId Reassignment
    1F81 01 00000004 80000007

    The same correction is to be done for object Index="1600" SubIndex="01" also.

    Hope this solves your problem.

    Regards,
    Powerlink-team
    Kalycito

     
  • Wolfgang Seiss

    Wolfgang Seiss - 2013-05-08

    Hi Sixten,

    The defaultValue in the XDD reflects - as the name indicates - the value that is contained in the object when it is not configured. If you want to set the mapping by default, you'd need to enter the value in the object dictionary of your device. Then your XDD would be correct.

    Otherwise, you have to tell the MN to write the mapping via SDO. openCONFIGURATOR will write the setting only to the CDC if the actualValue (i.e. the value requested by you) differs from the defaultValue.
    You can either do as Kalycito suggested (writing your value into an actualValue entry in the file) or you could enter the actualValue also in the openCONFIGURATOR GUI in the Value field of the mapping subobject (or via the PDO mapping table).

    Best regards,
    Wolfgang

     
  • Sixten Isaksson

    Sixten Isaksson - 2013-05-08

    Thank you so much for your help. Kalycito it worked just like you said. I had not noticed the ActualValue field. And thank you Wolfgang for your reply, it gave me a deeper understanding of the mapping between MN and CN.

    Best regards,
    Sixten

     