We are working with Vb.net y S7-1200 (firmware 4.0) and the connection to the PLC works, but I can't read anything from it. It always give me the following Error:
error 33028 context is not supported. Step7 says: Function not implemented or error in telegram.
Using same program and a PLC with firmware 3.0 run ok.
We tried enabled/disabled Optimize block access, but does not work.
I hope someone has any idea to solve the problem. Thanks!
I Have a some problem , do you have a solution ?
today I had tesed is OK,See attachments! first:DB must no protect,no Optimize,HMI may acess ,at the same must open Get/put protect
My email:zjx4051@gmail.com
We are working with Vb.net y S7-1200 (firmware 4.0) and the connection to the PLC works, but I can't read anything from it. It always give me the following Error:
Using same program and a PLC with firmware 3.0 run ok.
We tried enabled/disabled Optimize block access, but does not work.
I hope someone has any idea to solve the problem. Thanks!
I Have a some problem , do you have a solution ?
today I had tesed is OK,See attachments!
first:DB must no protect,no Optimize,HMI may acess ,at the same must open Get/put protect
My email:zjx4051@gmail.com