  • Paulo de Morais Oliveira Filho

    Hello guys, my name is Paulo

    I need some help with OpenDSS. I am running this circuit with loadshapes as loads and I put an energy meter in the beginning, attached to the transformer, but after running the simulation, when I open the CSV file of the energymeter, all of its values are "0" or "-1.00E+50". I have checked my script to see if there is any trouble, but i culdn't find it...all the values are okay, powers, voltages and etc...but the energy meter is getting nothing... Do you know what can it be? Thanks in advance!

    Informations that might be useful

    • my circuit is radial
    • duty simulation
    • all my loads are real data as loadshapes
     
  • Roger Dugan

    Roger Dugan - 2017-05-07

    The EnergyMeter object does not sample by default in DutyCycle mode. You can change the default by

    set sampleenergymeters=yes
    

    when the simulation is in Duty mode.

     
  • Paulo de Morais Oliveira Filho

    I have found the problem, Mr. Roger. The step I was using was 15 min. I found out that in this case, the best mode is daily, and it worked very well.

    Anyway, your information helped me a lot, thank you so much Mr. Dugan!

     