I am trying to read and write data from S7-200 Smart PLC from all possible locations using Settimino Library. But unable to do it as its not same as other PLCs.
Please let me know if its compatible. If YES then guide me through the protocol also the corresponding changes accordingly.
Awaiting Response,
Supriya.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Hello Mr. Nardella,
I am trying to read and write data from S7-200 Smart PLC from all possible locations using Settimino Library. But unable to do it as its not same as other PLCs.
Please let me know if its compatible. If YES then guide me through the protocol also the corresponding changes accordingly.
Awaiting Response,
Supriya.
You have to use SetConnectionParams() an then Connect().
Here you find S7200 related (for Snap7, but it's the same):
http://snap7.sourceforge.net/s7_200.html
Here you find LOGO related, which uses the same memory scheme of S7200 (they are very similar)
http://snap7.sourceforge.net/logo.html
I am consered about S7-200 SMART PLC. Here Step 7- Micro Win Smart V2.1 software is used. How we are supposed to get TSAP values?
I don't know Micro Win Smart, sorry.
Maybe this post can help you:
https://sourceforge.net/p/snap7/discussion/general/thread/ab55a131/
Thanks a lot for the quick answers.
Will keep you updated with the progress.
:-)