    Roy20 - 2023-07-06

    Hello,

    I need help using nettoplcsim. I want to simulate PCS7 OS Server which is located on a different Virtual machine than the ES. In principle, i have two virtual networks
    PlantBus on ES:192.168.250.5
    TerminalBus on ES: 192.168.251.5
    The CPU address is set to 192.168.250.101 and i can sucessfully download and go online with plc on the ES.

    However, the there is no communication between the plcsim on ES and the OS server. i followed the procedures according to the manual. The network address on nettoplm sim is set to 192.168.250.5 and the plc sim address is set to 192.158.250.101. On the network interface, i also added 192.168.250.101 as mentioned in one of the topics.
    The OS server Plantbus interface is: 192.168.250.10 and the terminalbus is 192.168.250.10. Can anyone please help to solve this issue? Thank you

     

    Last edit: Roy20 2023-07-06
  • Thomas Wiens

    Thomas Wiens - 2023-07-06

    OS Server terminalbus should have 192.168.251.10.

    The other settings are ok for me. Can you ping 192.168.250.101 from the OS server? And doese the browse dialog in Nettoplcsim for the Network interface find the interface with 192.168.250.101?

    And make sure that you have set the connection type between OS and Plc to TCP/IP, an Iso connection won't work with Nettoplcsim.

     