EIB object 12.001 not supported by linknx?

Help
Ronny
2011-03-01
2012-12-14
  • Ronny

    Ronny - 2011-03-01

    Hi
    I have a Merten actor 647895 wich detection of (electric) current. To count the watt per hours there is a object I can configure in ETS - ETS says it is 4 Byte and type 12.001 . So I added the following line to the linknx.xml file:

    <object type="12.001" id="strommessung.energieverbrauch.eg_flur_lichtdecke" gad="11/1/0" init="persist" log="true">EG_Flur_LichtDecke</object>

    When I now start up linknx it will shutdown with "1298995953 ERROR main : Error in config: Object type not supported: '12.001' "

    Is there a chance I can get this working with maybe a similar object type?

    Thanks a lot,
    Ronny

     
  • JensH

    JensH - 2011-03-01

    Hi Ronny, this are the supported objects:

    1.001 Switch
    3.007 Dimming
    3.008 Blinds
    5.xxx UInt (8bit)
    5.001 Scaling
    5.003 Angle
    6.xxx Signed (8bit)
    7.xxx Uint (16bit)
    8.xxx Signed (16bit)
    9.xxx Value  (floating 16bit)
    10.001 Time
    11.001 Date
    12.xxx Uint (32bit)
    13.xxx Signed (32bit)
    14.xxx Value32
    16.000 String
    20.102 HeatingMode

    In your case you pobably have to write "12.xxx"
    best Regards, Jens

     
  • Ronny

    Ronny - 2011-03-01

    Thanks a lot Jens this was the right hint - it now works! - sometimes its very simple :o)

     