Modbus RTU over TCP/IP

Help
2015-02-08
2015-09-14
  • José Manuel Pires

    Hello, I'm trying to implement a ModbusTCP Master with RTU compatibility. I have implemented a TCP Master and also a Serial Master, but I have no documentation on how to implement a RTU Master over TCP connection. Is there any information or example about this code implementation? Thanks in advance.

     
  • Julie Haugh

    Julie Haugh - 2015-09-14

    You make the requests "headless". This causes the 6 byte Modbus/TCP header to be ignored and the CRC to be added. The slave will receive the "RTU-formatted" request and respond with a "RTU-formatted" response. The master will then see that the request was headless and interpret the response data as an "RTU-formatted" response message.

    All that pretty much happens automatically for you, once you've indicated that the request itself is "headless".

     

Log in to post a comment.