Analog Output Holding Registers vs Analog Input Registers Reading Issue

Help
ascaso66
2014-06-10
2015-09-03
  • ascaso66

    ascaso66 - 2014-06-10

    Hi all,
    I'm a beginner on ModBus I/F, please excuse me.
    Using jamod I wrote a Slave on TCP that manages a pool of registers (Jamod SimpleInputRegister).
    When I use an external Server (not wrote by myself) and it reads the registers with the Function Code 3 everything works fine.
    If the Server reads the registers with the Function Code 4 I face a problem:
    An exception rise with the value Illegal Data Address.
    Probably this issue is due to my erroneous use of Analog Output Holding Registers vs Analog Input Registers.
    How can I do to solve my Slave issue ?
    Thanks in advance fior the help.
    :D
    Luca

     
  • Julie Haugh

    Julie Haugh - 2015-09-03

    Your Modbus/TCP slave needs to allow reads via wither FC 3 or FC 4 to use the same variables. You don't provide your slave source code, but I assume you are creating it using the "SimpleProcessImage" class that is using in many of the examples in this folder -

    https://sourceforge.net/p/j2mod/code/HEAD/tree/trunk/src/com/ghgande/j2mod/modbus/cmd/

    Assuming you're using a SimpleRegister() for your value, you would instead need to use a SimpleInputRegister() and pass that register object to both addRegister() and addInputRegister().

    If you are still having issues, you may want to convert your project to use j2mod, which is a fork of jamod that my company greenHouse Gas and Electric supports. You can find that project here -

    https://sourceforge.net/projects/j2mod/

     