In my openDSS file, a series of loads were added to a 3-phase bus (or collection of nodes) in this way:
New Load.671 Bus1=671.1.2.3 Phases=3 Conn=Delta Model=1 kV=4.16 kW=1155 kvar=660 New Load.671a Bus1=671.1 Phases=1 Conn=Wye Model=1 kV=4.16 kW=1 kvar=1 New Load.671b Bus1=671.2 Phases=1 Conn=Wye Model=1 kV=4.16 kW=1 kvar=1 New Load.671c Bus1=671.3 Phases=1 Conn=Wye Model=1 kV=4.16 kW=1 kvar=1
Then, if I run these lines through the Python interface, what would happen?
dssCircuit.SetActiveBus('671.1') dssCircuit.Loads.kW = 1000.0; dssCircuit.Loads.kvar = 500.0;
What I wanted to do is control 'Load.671a' only, but in the codewise, I cannot find the necessary distinction between 'Load.671' and 'Load.671a'.
Best Regards,
In Kwon Park
Hello,
Well, that's because you are doing it incorrectly. To select a load, you have to activate the load, not the bus, buses are not objects and are only used as a reference across the model. So, if you want to control load 671, do as follows:
dssCircuit.Loads.Name = '671'; dssCircuit.Loads.kW = 1000.0; dssCircuit.Loads.kvar = 500.0;
To go for load 671a, do as follows:
dssCircuit.Loads.Name = '671a'; dssCircuit.Loads.kW = 1000.0; dssCircuit.Loads.kvar = 500.0;
Please check the COM help file.
Best regards
Davis
Thank you for your answers! Certainly, I'll check the COM help file.
You have the wrong voltage for the three 1-phase loads. Should be kV=2.4.
Yes. You are absolutely right. It was my mistake, a result from careless copy and paste.
Log in to post a comment.
Hello there,
Would you allow me to ask this question?
In my openDSS file, a series of loads were added to a 3-phase bus (or collection of nodes) in this way:
New Load.671 Bus1=671.1.2.3 Phases=3 Conn=Delta Model=1 kV=4.16 kW=1155 kvar=660
New Load.671a Bus1=671.1 Phases=1 Conn=Wye Model=1 kV=4.16 kW=1 kvar=1
New Load.671b Bus1=671.2 Phases=1 Conn=Wye Model=1 kV=4.16 kW=1 kvar=1
New Load.671c Bus1=671.3 Phases=1 Conn=Wye Model=1 kV=4.16 kW=1 kvar=1
Then, if I run these lines through the Python interface, what would happen?
What I wanted to do is control 'Load.671a' only, but in the codewise, I cannot find the necessary distinction between 'Load.671' and 'Load.671a'.
Best Regards,
In Kwon Park
Hello,
Well, that's because you are doing it incorrectly. To select a load, you have to activate the load, not the bus, buses are not objects and are only used as a reference across the model. So, if you want to control load 671, do as follows:
To go for load 671a, do as follows:
Please check the COM help file.
Best regards
Davis
Hello,
Thank you for your answers!
Certainly, I'll check the COM help file.
Best Regards,
In Kwon Park
You have the wrong voltage for the three 1-phase loads. Should be kV=2.4.
Yes. You are absolutely right. It was my mistake, a result from careless copy and paste.
In Kwon Park