Add a 1-Phase transformer and PV system to IEEE 37 bus

2018-07-02
2018-07-06
  • Paddysomnang

    Paddysomnang - 2018-07-02

    Dear all,
    I am working on the IEEE37 test feeder. I am trying to add 5KW PF=1 PV system to the bus 775. I also add a single phase transformer at the bus 709s. Since I am a starter for this software, I do not know whether my single phase transformer and PV system model is correct or not ?
    Could anyone help me checking my model, please? Please help me to correct if there is anything wrong with my 3-phase transformer at bus 799, 1-phase transformer at bus 709 and 5-KW PV system at bus 775.
    The voltage at bus 775 suppose to be 0.97796 p.u, angle= -31.9° but I can't get it.
    I have attached the data, code and diagram of my modified IEEE37 bus below.
    Thank you for your help.

    Best Regards,

     

    Last edit: Paddysomnang 2018-07-02
  • Roger Dugan

    Roger Dugan - 2018-07-02

    Let's start with one thing and see what happens ....

    You must understand the distribution system you are modeling and OpenDSS is a good teacher. This is a 3-wire delta system, so there is nothing stabilizing the neutral. So you don't connect 1-phase transformers line-to-neutral (actually, line-to-ground). You would connect the primary line-to-line. Change the connection and primary kV rating of the 1-phase transformer and work from there.

     
  • Paddysomnang

    Paddysomnang - 2018-07-02

    Dear Roger Dugan and everyone,
    Thank you for your reply. I am not sure I fully understand your reply or not. but I have made a few changes to my single phase transformer.
    Could you please correct me if it is still wrong?
    Thank you.

    Clear
    Set DefaultBaseFrequency=60

    New object=circuit.ieee37
    ~ basekv=138 pu=1.00 MVAsc3=200000 MVAsc1=210000

    ! Substation Transformer
    New Transformer.SubXF Phases=3 Windings=2 Xhl=0.8
    ~ wdg=1 bus=sourcebus conn=Delta kv=138 kva=5000 %r=8
    ~ wdg=2 bus=799 conn=Delta kv=4.16 kva=5000 %r=8

    !Regulator
    new transformer.reg1a phases=1 windings=2 bank=reg1 buses=(799.1.2 799r.1.2) conns='wye wye' kvs="4.16 4.16" kvas="2000 2000" XHL=1
    new regcontrol.creg1a transformer=reg1a winding=2 vreg=124 band=2 ptratio=20 ctprim=700
    new transformer.reg1b phases=1 windings=2 bank=reg1 buses=(799.2.3 799r.2.3) conns='wye wye' kvs="4.16 4.16" kvas="2000 2000" XHL=1
    new regcontrol.creg1b transformer=reg1b winding=2 vreg=124 band=2 ptratio=20 ctprim=700
    new transformer.reg1c phases=1 windings=2 bank=reg1 buses=(799.3.1 799r.3.1) conns='wye wye' kvs="4.16 4.16" kvas="2000 2000" XHL=1
    new regcontrol.creg1c transformer=reg1c winding=2 vreg=124 band=2 ptratio=20 ctprim=700

    ! Load Transformer
    New Transformer.XFM1 Phases=1 Windings=2 Xhl=1
    ~ wdg=1 bus=709.1 conn=Delta kv=4.16 kva=10 %r=3
    ~ wdg=2 bus=709s.1.0 conn=Delta kv=0.12 kva=10 %r=3

    ! import line codes with phase impedance matrices
    Redirect IEEELineCodes.dss

    ! Lines
    New Line.L1 Phases=3 Bus1=701.1.2.3 Bus2=702.1.2.3 LineCode=722 Length=0.96
    New Line.L2 Phases=3 Bus1=702.1.2.3 Bus2=705.1.2.3 LineCode=724 Length=0.4
    New Line.L3 Phases=3 Bus1=702.1.2.3 Bus2=713.1.2.3 LineCode=723 Length=0.36
    New Line.L4 Phases=3 Bus1=702.1.2.3 Bus2=703.1.2.3 LineCode=722 Length=1.32
    New Line.L5 Phases=3 Bus1=703.1.2.3 Bus2=727.1.2.3 LineCode=724 Length=0.24
    New Line.L6 Phases=3 Bus1=703.1.2.3 Bus2=730.1.2.3 LineCode=723 Length=0.6
    New Line.L7 Phases=3 Bus1=704.1.2.3 Bus2=714.1.2.3 LineCode=724 Length=0.08
    New Line.L8 Phases=3 Bus1=704.1.2.3 Bus2=720.1.2.3 LineCode=723 Length=0.8
    New Line.L9 Phases=3 Bus1=705.1.2.3 Bus2=742.1.2.3 LineCode=724 Length=0.32
    New Line.L10 Phases=3 Bus1=705.1.2.3 Bus2=712.1.2.3 LineCode=724 Length=0.24
    New Line.L11 Phases=3 Bus1=706.1.2.3 Bus2=725.1.2.3 LineCode=724 Length=0.28
    New Line.L12 Phases=3 Bus1=707.1.2.3 Bus2=724.1.2.3 LineCode=724 Length=0.76
    New Line.L13 Phases=3 Bus1=707.1.2.3 Bus2=722.1.2.3 LineCode=724 Length=0.12
    New Line.L14 Phases=3 Bus1=708.1.2.3 Bus2=733.1.2.3 LineCode=723 Length=0.32
    New Line.L15 Phases=3 Bus1=708.1.2.3 Bus2=732.1.2.3 LineCode=724 Length=0.32
    New Line.L16 Phases=3 Bus1=709.1.2.3 Bus2=731.1.2.3 LineCode=723 Length=0.6
    New Line.L17 Phases=3 Bus1=709.1.2.3 Bus2=708.1.2.3 LineCode=723 Length=0.32
    New Line.L18 Phases=3 Bus1=710.1.2.3 Bus2=735.1.2.3 LineCode=724 Length=0.2
    New Line.L19 Phases=3 Bus1=710.1.2.3 Bus2=736.1.2.3 LineCode=724 Length=1.28
    New Line.L20 Phases=3 Bus1=711.1.2.3 Bus2=741.1.2.3 LineCode=723 Length=0.4
    New Line.L21 Phases=3 Bus1=711.1.2.3 Bus2=740.1.2.3 LineCode=724 Length=0.2
    New Line.L22 Phases=3 Bus1=713.1.2.3 Bus2=704.1.2.3 LineCode=723 Length=0.52
    New Line.L23 Phases=3 Bus1=714.1.2.3 Bus2=718.1.2.3 LineCode=724 Length=0.52
    New Line.L24 Phases=3 Bus1=720.1.2.3 Bus2=707.1.2.3 LineCode=724 Length=0.92
    New Line.L25 Phases=3 Bus1=720.1.2.3 Bus2=706.1.2.3 LineCode=723 Length=0.6
    New Line.L26 Phases=3 Bus1=727.1.2.3 Bus2=744.1.2.3 LineCode=723 Length=0.28
    New Line.L27 Phases=3 Bus1=730.1.2.3 Bus2=709.1.2.3 LineCode=723 Length=0.2
    New Line.L28 Phases=3 Bus1=733.1.2.3 Bus2=734.1.2.3 LineCode=723 Length=0.56
    New Line.L29 Phases=3 Bus1=734.1.2.3 Bus2=737.1.2.3 LineCode=723 Length=0.64
    New Line.L30 Phases=3 Bus1=734.1.2.3 Bus2=710.1.2.3 LineCode=724 Length=0.52
    New Line.L31 Phases=3 Bus1=737.1.2.3 Bus2=738.1.2.3 LineCode=723 Length=0.4
    New Line.L32 Phases=3 Bus1=738.1.2.3 Bus2=711.1.2.3 LineCode=723 Length=0.4
    New Line.L33 Phases=3 Bus1=744.1.2.3 Bus2=728.1.2.3 LineCode=724 Length=0.2
    New Line.L34 Phases=3 Bus1=744.1.2.3 Bus2=729.1.2.3 LineCode=724 Length=0.28
    New Line.L35 Phases=3 Bus1=799r.1.2.3 Bus2=701.1.2.3 LineCode=721 Length=1.85
    New Line.L36 Phases=1 Bus1=709s.1 Bus2=775.1 LineCode=721 length=0.03048

    ! spot loads
    New Load.S701a Bus1=701.1.2 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 140.0 kVAR= 70.0
    New Load.S701b Bus1=701.2.3 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 140.0 kVAR= 70.0
    New Load.S701c Bus1=701.3.1 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 350.0 kVAR= 175.0
    New Load.S712c Bus1=712.3.1 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S713c Bus1=713.3.1 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S714a Bus1=714.1.2 Phases=1 Conn=Delta Model=4 kV= 4.800 kW= 17.0 kVAR= 8.0
    New Load.S714b Bus1=714.2.3 Phases=1 Conn=Delta Model=4 kV= 4.800 kW= 21.0 kVAR= 10.0
    New Load.S718a Bus1=718.1.2 Phases=1 Conn=Delta Model=2 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S720c Bus1=720.3.1 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S722b Bus1=722.2.3 Phases=1 Conn=Delta Model=4 kV= 4.800 kW= 140.0 kVAR= 70.0
    New Load.S722c Bus1=722.3.1 Phases=1 Conn=Delta Model=4 kV= 4.800 kW= 21.0 kVAR= 10.0
    New Load.S724b Bus1=724.2.3 Phases=1 Conn=Delta Model=2 kV= 4.800 kW= 42.0 kVAR= 21.0
    New Load.S725b Bus1=725.2.3 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 42.0 kVAR= 21.0
    New Load.S727c Bus1=727.3.1 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 42.0 kVAR= 21.0
    New Load.S728 Bus1=728 Phases=3 Conn=Delta Model=1 kV= 4.800 kW= 126.0 kVAR= 63.0
    New Load.S729a Bus1=729.1.2 Phases=1 Conn=Delta Model=4 kV= 4.800 kW= 42.0 kVAR= 21.0
    New Load.S730c Bus1=730.3.1 Phases=1 Conn=Delta Model=2 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S731b Bus1=731.2.3 Phases=1 Conn=Delta Model=2 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S732c Bus1=732.3.1 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 42.0 kVAR= 21.0
    New Load.S733a Bus1=733.1.2 Phases=1 Conn=Delta Model=4 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S734c Bus1=734.3.1 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 42.0 kVAR= 21.0
    New Load.S735c Bus1=735.3.1 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S736b Bus1=736.2.3 Phases=1 Conn=Delta Model=2 kV= 4.800 kW= 42.0 kVAR= 21.0
    New Load.S737a Bus1=737.1.2 Phases=1 Conn=Delta Model=4 kV= 4.800 kW= 140.0 kVAR= 70.0
    New Load.S738a Bus1=738.1.2 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 126.0 kVAR= 62.0
    New Load.S740c Bus1=740.3.1 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S741c Bus1=741.3.1 Phases=1 Conn=Delta Model=4 kV= 4.800 kW= 42.0 kVAR= 21.0
    New Load.S742a Bus1=742.1.2 Phases=1 Conn=Delta Model=2 kV= 4.800 kW= 8.0 kVAR= 4.0
    New Load.S742b Bus1=742.2.3 Phases=1 Conn=Delta Model=2 kV= 4.800 kW= 85.0 kVAR= 40.0
    New Load.S744a Bus1=744.1.2 Phases=1 Conn=Delta Model=1 kV= 4.800 kW= 42.0 kVAR= 21.0

    ! ADD 5-KW PV System, power factor 1
    // P-T curve is per unit of rated Pmpp vs temperature
    // This one is for a Pmpp stated at 25 deg
    New XYCurve.MyPvsT npts=4 xarray=[0 25 75 100] yarray=[1.2 1.0 0.8 0.6]

    // efficiency curve is per unit eff vs per unit power
    New XYCurve.MyEff npts=4 xarray=[.1 .2 .4 1.0] yarray=[.86 .9 .93 .97]

    // per unit irradiance curve (per unit if "irradiance" property)
    New Loadshape.MyIrrad npts=24 interval=1 mult=[0 0 0 0 0 0 .1 .2 .3 .5 .8 .9 1.0 1.0 .99 .9 .7 .4 .1 0 0 0 0 0 ]
    !mult=(File=irradiance.csv)

    // 24-hr temp shape curve
    New Tshape.MyTemp npts=24 interval=1 temp=[25 25 25 25 25 25 25 25 35 40 45 50 60 60 55 40 35 30 25 25 25 25 25 25 ]
    !(File=temperature.csv)

    // pv definition
    New PVSystem.PV phases=1 bus1=775.1 kV=0.12 kVA=5 irrad=.98 Pmpp=500 temperature=25 PF=1
    %cutin=0.1 %cutout=0.1 effcurve=Myeff P-TCurve=MyPvsT Daily=MyIrrad TDaily=MyTemp !default for inverter is unity PF

    Set VoltageBases = "138,4.16,0.12"
    CalcVoltageBases
    BusCoords IEEE37_BusXY.csv

    ! solve mode=direct
    set maxiterations=100
    solve

    ! show voltages LL Nodes
    ! show currents residual=y elements
    ! show powers kva elements
    ! show taps

     
  • Roger Dugan

    Roger Dugan - 2018-07-06

    Change the Load Transformer definition to the following:

    ! Load Transformer
    New Transformer.XFM1 Phases=1 Windings=2 Xhl=1
    ~ wdg=1 bus=709.1.2 conn=Delta kv=4.16 kva=10 %r=3
    ~ wdg=2 bus=709s.1.0 conn=Delta kv=0.12 kva=10 %r=3
    
     