Error in SwtControl function in OpenDSS

Zhraso
2020-03-11
2020-03-25
  • Zhraso

    Zhraso - 2020-03-11

    Hello All,

    I want to consider a switch on a line using following code for a modified IEEE 13-bus system with a new line added. I define a switch on the new line using:

    New SwtControl.680675 SwitchedObj=Line.680675 SwitchedTerm=1 Action=Open Lock=Yes Delay=0 Normal=Open

    However, when I run the code the line is still close. How can I open Line.680675 ?

    Also, I want to consider three switches for Line.680675 (i.e., one switch for each phase of the line), How can I define one switch for each phase of this line and control them independently?

    Thanks

    Here is the code:

    Clear

    !
    ! This script is based on a script developed by Tennessee Tech Univ students
    ! Tyler Patton, Jon Wood, and David Woods, April 2009
    !

    new circuit.IEEE13Nodeckt
    ~ basekv=115 pu=1.0001 phases=3 bus1=SourceBus
    ~ Angle=30 ! advance angle 30 deg so result agree with published angle
    ~ MVAsc3=20000 MVASC1=21000 ! stiffen the source to approximate inf source

    !SUB TRANSFORMER DEFINITION
    ! Although this data was given, it does not appear to be used in the test case results
    ! The published test case starts at 1.0 per unit at Bus 650. To make this happen, we will change the impedance
    ! on the transformer to something tiny by dividing by 1000 using the DSS in-line RPN math
    New Transformer.Sub Phases=3 Windings=2 XHL=(8 1000 /)
    ~ wdg=1 bus=SourceBus conn=delta kv=115 kva=5000 %r=(.5 1000 /) XHT=4
    ~ wdg=2 bus=650 conn=wye kv=4.16 kva=5000 %r=(.5 1000 /) XLT=4

    ! FEEDER 1-PHASE VOLTAGE REGULATORS
    ! Define low-impedance 2-wdg transformer

    New Transformer.Reg1 phases=1 XHL=0.01 kVAs=[1666 1666]
    ~ Buses=[650.1 RG60.1] kVs=[2.4 2.4] %LoadLoss=0.01
    new regcontrol.Reg1 transformer=Reg1 winding=2 vreg=122 band=2 ptratio=20 ctprim=700 R=3 X=9

    New Transformer.Reg2 phases=1 XHL=0.01 kVAs=[1666 1666]
    ~ Buses=[650.2 RG60.2] kVs=[2.4 2.4] %LoadLoss=0.01
    new regcontrol.Reg2 transformer=Reg2 winding=2 vreg=122 band=2 ptratio=20 ctprim=700 R=3 X=9

    New Transformer.Reg3 phases=1 XHL=0.01 kVAs=[1666 1666]
    ~ Buses=[650.3 RG60.3] kVs=[2.4 2.4] %LoadLoss=0.01
    new regcontrol.Reg3 transformer=Reg3 winding=2 vreg=122 band=2 ptratio=20 ctprim=700 R=3 X=9

    !TRANSFORMER DEFINITION
    New Transformer.XFM1 Phases=3 Windings=2 XHL=2
    ~ wdg=1 bus=633 conn=Wye kv=4.16 kva=500 %r=.55 XHT=1
    ~ wdg=2 bus=634 conn=Wye kv=0.480 kva=500 %r=.55 XLT=1

    !LINE CODES
    redirect IEEELineCodes.dss

    // these are local matrix line codes
    // corrected 9-14-2011
    New linecode.mtx601 nphases=3 BaseFreq=60
    ~ rmatrix = (0.3465 | 0.1560 0.3375 | 0.1580 0.1535 0.3414 )
    ~ xmatrix = (1.0179 | 0.5017 1.0478 | 0.4236 0.3849 1.0348 )
    ~ units=mi
    New linecode.mtx602 nphases=3 BaseFreq=60
    ~ rmatrix = (0.7526 | 0.1580 0.7475 | 0.1560 0.1535 0.7436 )
    ~ xmatrix = (1.1814 | 0.4236 1.1983 | 0.5017 0.3849 1.2112 )
    ~ units=mi
    New linecode.mtx603 nphases=2 BaseFreq=60
    ~ rmatrix = (1.3238 | 0.2066 1.3294 )
    ~ xmatrix = (1.3569 | 0.4591 1.3471 )
    ~ units=mi
    New linecode.mtx604 nphases=2 BaseFreq=60
    ~ rmatrix = (1.3238 | 0.2066 1.3294 )
    ~ xmatrix = (1.3569 | 0.4591 1.3471 )
    ~ units=mi
    New linecode.mtx605 nphases=1 BaseFreq=60
    ~ rmatrix = (1.3292 )
    ~ xmatrix = (1.3475 )
    ~ units=mi

    / Original 606 Linecode ****

    You have to use this to match Kersting's results:

    New linecode.mtx606 nphases=3 BaseFreq=60
    ~ rmatrix = (0.7982 | 0.3192 0.7891 | 0.2849 0.3192 0.7982 )
    ~ xmatrix = (0.4463 | 0.0328 0.4041 | -0.0143 0.0328 0.4463 )
    ~ Cmatrix = [257 | 0 257 | 0 0 257] ! <--- This is too low by 1.5
    ~ units=mi

    Corrected mtx606 Feb 3 2016 by RDugan

    The new LineCode.606 is computed using the following CN cable definition and
    LineGeometry definition:

    New CNDATA.250_1/3 k=13 DiaStrand=0.064 Rstrand=2.816666667 epsR=2.3
    ~ InsLayer=0.220 DiaIns=1.06 DiaCable=1.16 Rac=0.076705 GMRac=0.20568 diam=0.573
    ~ Runits=kft Radunits=in GMRunits=in

    New LineGeometry.606 nconds=3 nphases=3 units=ft
    ~ cond=1 cncable=250_1/3 x=-0.5 h= -4
    ~ cond=2 cncable=250_1/3 x=0 h= -4
    ~ cond=3 cncable=250_1/3 x=0.5 h= -4

    End Comment**/

    New Linecode.mtx606 nphases=3 Units=mi
    ~ Rmatrix=[0.791721 |0.318476 0.781649 |0.28345 0.318476 0.791721 ]
    ~ Xmatrix=[0.438352 |0.0276838 0.396697 |-0.0184204 0.0276838 0.438352 ]
    ~ Cmatrix=[383.948 |0 383.948 |0 0 383.948 ]
    New linecode.mtx607 nphases=1 BaseFreq=60
    ~ rmatrix = (1.3425 )
    ~ xmatrix = (0.5124 )
    ~ cmatrix = [236]
    ~ units=mi

    !LOAD DEFINITIONS
    New Load.671 Bus1=671.1.2.3 Phases=3 Conn=Delta Model=1 kV=4.16 kW=1155 kvar=660
    New Load.634a Bus1=634.1 Phases=1 Conn=Wye Model=1 kV=0.277 kW=160 kvar=110
    New Load.634b Bus1=634.2 Phases=1 Conn=Wye Model=1 kV=0.277 kW=120 kvar=90
    New Load.634c Bus1=634.3 Phases=1 Conn=Wye Model=1 kV=0.277 kW=120 kvar=90
    New Load.645 Bus1=645.2 Phases=1 Conn=Wye Model=1 kV=2.4 kW=170 kvar=125
    New Load.646 Bus1=646.2.3 Phases=1 Conn=Delta Model=2 kV=4.16 kW=230 kvar=132
    New Load.692 Bus1=692.3.1 Phases=1 Conn=Delta Model=5 kV=4.16 kW=170 kvar=151
    New Load.675a Bus1=675.1 Phases=1 Conn=Wye Model=1 kV=2.4 kW=485 kvar=190
    New Load.675b Bus1=675.2 Phases=1 Conn=Wye Model=1 kV=2.4 kW=68 kvar=60
    New Load.675c Bus1=675.3 Phases=1 Conn=Wye Model=1 kV=2.4 kW=290 kvar=212
    New Load.611 Bus1=611.3 Phases=1 Conn=Wye Model=5 kV=2.4 kW=170 kvar=80
    New Load.652 Bus1=652.1 Phases=1 Conn=Wye Model=2 kV=2.4 kW=128 kvar=86
    New Load.670a Bus1=670.1 Phases=1 Conn=Wye Model=1 kV=2.4 kW=17 kvar=10
    New Load.670b Bus1=670.2 Phases=1 Conn=Wye Model=1 kV=2.4 kW=66 kvar=38
    New Load.670c Bus1=670.3 Phases=1 Conn=Wye Model=1 kV=2.4 kW=117 kvar=68

    !CAPACITOR DEFINITIONS
    New Capacitor.Cap1 Bus1=675 phases=3 kVAR=600 kV=4.16
    New Capacitor.Cap2 Bus1=611.3 phases=1 kVAR=100 kV=2.4

    !Bus 670 is the concentrated point load of the distributed load on line 632 to 671 located at 1/3 the distance from node 632

    !LINE DEFINITIONS
    New Line.650632 Phases=3 Bus1=RG60.1.2.3 Bus2=632.1.2.3 LineCode=mtx601 Length=2000 units=ft
    New Line.632670 Phases=3 Bus1=632.1.2.3 Bus2=670.1.2.3 LineCode=mtx601 Length=667 units=ft
    New Line.670671 Phases=3 Bus1=670.1.2.3 Bus2=671.1.2.3 LineCode=mtx601 Length=1333 units=ft
    New Line.671680 Phases=3 Bus1=671.1.2.3 Bus2=680.1.2.3 LineCode=mtx601 Length=1000 units=ft
    New Line.632633 Phases=3 Bus1=632.1.2.3 Bus2=633.1.2.3 LineCode=mtx602 Length=500 units=ft
    New Line.632645 Phases=2 Bus1=632.3.2 Bus2=645.3.2 LineCode=mtx603 Length=500 units=ft
    New Line.645646 Phases=2 Bus1=645.3.2 Bus2=646.3.2 LineCode=mtx603 Length=300 units=ft
    New Line.692675 Phases=3 Bus1=692.1.2.3 Bus2=675.1.2.3 LineCode=mtx606 Length=500 units=ft
    New Line.671684 Phases=2 Bus1=671.1.3 Bus2=684.1.3 LineCode=mtx604 Length=300 units=ft
    New Line.684611 Phases=1 Bus1=684.3 Bus2=611.3 LineCode=mtx605 Length=300 units=ft
    New Line.684652 Phases=1 Bus1=684.1 Bus2=652.1 LineCode=mtx607 Length=800 units=ft

    New Line.680675 Phases=3 Bus1=680.1.2.3 Bus2=675.1.2.3 LineCode=mtx601 Length=1000 units=ft

    !SWITCH DEFINITIONS
    New Line.671692 Phases=3 Bus1=671 Bus2=692 Switch=y r1=1e-4 r0=1e-4 x1=0.000 x0=0.000 c1=0.000 c0=0.000

    New SwtControl.680675 SwitchedObj=Line.680675 SwitchedTerm=1 Action=Open Lock=Yes Delay=0 Normal=Open
    Set Voltagebases=[115, 4.16, .48]
    calcv

    New Energymeter.meter element=Line.650632 terminal=1

    BusCoords IEEE13Node_BusXY.csv

    Solve
    !---------------------------------------------------------------------------------------------------------------------------------------------------
    !----------------Show some Results -----------------------------------------------------------------------------------------------------------------
    !---------------------------------------------------------------------------------------------------------------------------------------------------

    //Plot profile phases=all
    //Show Voltages LN Nodes
    // Show Currents Elem
    // Show Powers kVA Elem
    // Show Losses
    // Show Taps

    !---------------------------------------------------------------------------------------------------------------------------------------------------
    !---------------------------------------------------------------------------------------------------------------------------------------------------
    ! Alternate Solution Script
    ! To force the taps to be same as published results, set the transformer taps manually and disable the controls
    !---------------------------------------------------------------------------------------------------------------------------------------------------
    /*
    Transformer.Reg1.Taps=[1.0 1.0625]
    Transformer.Reg2.Taps=[1.0 1.0500]
    Transformer.Reg3.Taps=[1.0 1.06875]
    Set Controlmode=OFF

    Solve

     
    • Davis Montenegro

      Hello,

      The problem is simple, when disabling the control actions (Controlmode=OFF) the controllers, including the SwtControl, will not operate. If what you want to do is to open the line with no control actions, use the command "Open":

      Open Line.671692 1
      

      To close it back, use the command "Close" in the same way.

      Best regards

      Davis

       

      Last edit: Davis Montenegro 2020-03-25