I have a 1734-AENT with IB8, OB8E, IB8 . Rack size is configured = 4.
When I run the solution, I got the error:
An unhandled exception of type 'Sres.Net.EEIP.CIPException' occurred in EEIP.dll
Connection failure, General Status Code: 1 Additional Status Code: 789 Invalid segment in connection path
I tried to adjust eeipClient.O_T_Length & eeipClient.T_O_Length, but debug still show their lengths are both at 505.
TIA for any help.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I found the problem. The code sample from the site , as well as the YouTube video (https://www.youtube.com/watch?v=NLCXnVpDgl4 ) are really misleading.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
I have a 1734-AENT with IB8, OB8E, IB8 . Rack size is configured = 4.
When I run the solution, I got the error:
An unhandled exception of type 'Sres.Net.EEIP.CIPException' occurred in EEIP.dll
Connection failure, General Status Code: 1 Additional Status Code: 789 Invalid segment in connection path
I tried to adjust eeipClient.O_T_Length & eeipClient.T_O_Length, but debug still show their lengths are both at 505.
TIA for any help.
I found the problem. The code sample from the site , as well as the YouTube video (https://www.youtube.com/watch?v=NLCXnVpDgl4 ) are really misleading.
Hello, I am currently experiencing a similar issue. Could you please tell me what changes we made to resolve the issue.
Thankyou
sorry for the delay. see here:
https://www.advancedhmi.com/forum/index.php?topic=3187.0