Binary_Input_Write_Property

2023-04-17
2023-06-06
  • kishore venki

    kishore venki - 2023-04-17

    Hi,

    Binary_Input.PV can also be writeable if its Out_Of-Service(OOS) is set to TRUE similar to Analog , Multi-State-Input objects. But the checking of OOS is not there in the Binary_Input_Write_Property method. Below is the code snippet from version 1.0.0. Am I missing something?

    switch (wp_data->object_property) {
    case PROP_PRESENT_VALUE:
    status =
    WPValidateArgType(&value, BACNET_APPLICATION_TAG_
    &wp_data->error_class, &wp_data->error_code);
    if (status) {
    if (value.type.Enumerated <= MAX_BINARY_PV) {
    Binary_Input_Present_Value_Set(wp_data->object_instance,
    (BACNET_BINARY_PV)value.type.Enumerated);

     
  • Steve Karg

    Steve Karg - 2023-06-06

    The rule in BACnet for Present_Value properties that are associated with Out_Of_Service is that Present_Value must be writable when Out_Of_Service is true.

    The inverse(s) is not required, however. If Out_Of_Service is not configurable or writable to true (it is always false), then Present_Value is never required to be writable (except for commandable objects - i.e. Output objects). Also, Present_Value is allowed to be writable, even if Out_Of_Service is false.

     

    Last edit: Steve Karg 2023-06-06