    First of all, thank you so much for this great software.

    I'm having problems keeping the HMI connected to a SLC505 via ethernet. I have a form with several basic labels reading integer words and writing to them as well. Reading from the PLC stops after about 5-7 minutes of running the application, but I can still write to the registers with no problems at all. I have the poll override field on the driver set to 2000 and everything else to default. I have this problem with all the PLCs I have connected to, SLC505s and ML1100s. Any help or ideas will be greatly appreciated. Thanks.

     
  • Archie

    Archie - 2011-12-09

    Which version are you using? There was a fix in 3.21 that resolved an issue with data updates stopping after a short period of time in the SLC driver.

     
  • Jose J Garcia

    Jose J Garcia - 2011-12-09

    I'm still using 3.20, will go ahead and update and I'll report how it turns out. Thanks for the help.

     
  • Jose J Garcia

    Jose J Garcia - 2012-01-31

    I finally had a chance to update to 3.21, seems like the problem went away. Thanks for all your help.

     