First of all, thank you so much for this great software.
I'm having problems keeping the HMI connected to a SLC505 via ethernet. I have a form with several basic labels reading integer words and writing to them as well. Reading from the PLC stops after about 5-7 minutes of running the application, but I can still write to the registers with no problems at all. I have the poll override field on the driver set to 2000 and everything else to default. I have this problem with all the PLCs I have connected to, SLC505s and ML1100s. Any help or ideas will be greatly appreciated. Thanks.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
First of all, thank you so much for this great software.
I'm having problems keeping the HMI connected to a SLC505 via ethernet. I have a form with several basic labels reading integer words and writing to them as well. Reading from the PLC stops after about 5-7 minutes of running the application, but I can still write to the registers with no problems at all. I have the poll override field on the driver set to 2000 and everything else to default. I have this problem with all the PLCs I have connected to, SLC505s and ML1100s. Any help or ideas will be greatly appreciated. Thanks.
Which version are you using? There was a fix in 3.21 that resolved an issue with data updates stopping after a short period of time in the SLC driver.
I'm still using 3.20, will go ahead and update and I'll report how it turns out. Thanks for the help.
I finally had a chance to update to 3.21, seems like the problem went away. Thanks for all your help.