Problem with a Major error

Help
michele
2012-04-05
2013-05-30
  • michele

    michele - 2012-04-05

    I'm using your Ethernet/IP driver with success on a micrologix 1400 ser. B.
    Basically i just use the ReadAny function in a multithread cycle reading many tags, and write some set points.
    Everything is working good but once every 2-3 days i have a strange fault on PLC that says " Major error 71h: The controller cannot communicate with the expansion I/O module. Exact module cannot be determined".
    What we do is just reset the fault and it works again for 1-2 days.
    It can't be because of the communication driver right ?

     
  • michele

    michele - 2012-04-18

    It was a problem because of lack of suppressors on output relays…

     