The AdvancedHMI driver uses the first digit to translate to a function code. So for any address in the address picker showing a function code of 1 will need a leading 0. The address you need to use for the counter is 016385
Last edit: Archie 2015-09-14
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
That fixed the logic bits. All is working fine thanks.
Both the Modbus RTU & AB DF1 are working, but I still heve the warning in both.
Any ideas why?
I am using the latest Microsoft Community edition 2015.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Testing the latest Version 3.98 ModbusRTUCom1 on an Automation Direct Click PLC.
C logic bits displays an illegal data.
C1 Modbus 984 address 16385.
I get the warning:
Warning Could not find rule set file "Migrated rules for AdvancedHMI.ruleset". AdvancedHMI
The AdvancedHMI driver uses the first digit to translate to a function code. So for any address in the address picker showing a function code of 1 will need a leading 0. The address you need to use for the counter is 016385
Last edit: Archie 2015-09-14
You may want to see this post for some helpful tips on the Modbus driver:
http://advancedhmi.com/forum/index.php?topic=765.0
That fixed the logic bits. All is working fine thanks.
Both the Modbus RTU & AB DF1 are working, but I still heve the warning in both.
Any ideas why?
I am using the latest Microsoft Community edition 2015.
You can get rid of that warning by doing this: