i am trying to set up a selector switch for a AB micrologix 1000
I am using b3:0/1 as the switch address to turn on b3:0/2
when i do a debug test, it says write failed invalid address. I have a panel meter working reading the acc of a timer and a momentary push button that resets it like your example showed and they are working good.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
Check all of the PLCAddress properties for the selector switch and make sure the ones you are not using are blank. Some of the controls will fill in a default address.
If you would like to refer to this comment somewhere else in this project, copy and paste the following link:
i am trying to set up a selector switch for a AB micrologix 1000
I am using b3:0/1 as the switch address to turn on b3:0/2
when i do a debug test, it says write failed invalid address. I have a panel meter working reading the acc of a timer and a momentary push button that resets it like your example showed and they are working good.
Check all of the PLCAddress properties for the selector switch and make sure the ones you are not using are blank. Some of the controls will fill in a default address.